The electrical engineer had this input on calculating HP
110 vac is not the calculation just the min you need to run the unit. US is 115/120 v and the calculation usually assume 120v
2 hp specs are 120x13 is 1.6 k watts
Line voltage in the US is not 110 but that is the min it can be
3 hp specs is 120x 20 amps 2400 watts max
If he wants to use the 110 number x20 is 2.2k